Hipot is an abbreviation for high potential. Traditionally,
Hipot is a term given to a class of electrical safety
testing instruments used to verify electrical insulation
in finished appliances, cables or other wired assemblies,
printed circuit boards, electric motors, and transformers.
Under
normal conditions, any electrical device will produce
a minimal amount of leakage current due to the voltages
and internal capacitance present within the product.
Yet due to design flaws or other factors, the insulation
in a product can break down, resulting in excessive
leakage current flow. This failure condition can cause
shock or death to anyone that comes into contact with
the faulty product.
A
Hipot test (also called a Dielectric Withstand test)
verifies that the insulation of a product or component
is sufficient to protect the operator from electrical
shock. In a typical Hipot test, high voltage is applied
between a product's current-carrying conductors and
its metallic chassis. The resulting current that flows
through the insulation, known as leakage current, is
monitored by the hipot tester. The theory behind the
test is that if a deliberate over-application of test
voltage does not cause the insulation to break down,
the product will be safe to use under normal operating
conditions¡Xhence the name, Dielectric Withstand test.
In
addition to over-stressing the insulation, the test
can also be performed to detect material and workmanship
defects, most importantly small gap spacings between
current-carrying conductors and earth ground. When a
product is operated under normal conditions, environmental
factors such as humidity, dirt, vibration, shock and
contaminants can close these small gaps and allow current
to flow. This condition can create a shock hazard if
the defects are not corrected at the factory. No other
test can uncover this type of defect as well as the
Dielectric Withstand test.
Three
types of Hipot tests are commonly used. These three
tests differ in the amount of voltage applied and the
amount (or nature) of acceptable current flow:
Dielectric
breakdown Test. The test voltage is increased until
the dielectric fails, or breaks down, allowing too much
current to flow. The dielectric is often destroyed by
this test so this test is used on a random sample basis.
This test allows designers to estimate the breakdown
voltage of a product's design.
Dielectric
Withstand Test. A standard test voltage is applied (below
the established Breakdown Voltage) and the resulting
leakage current is monitored. The leakage current must
be below a preset limit or the test is considered to
have failed. This test is non-destructive and is usually
required by safety agencies to be performed as a 100%
production line test on all products before they leave
the factory.
Insulation
Resistance Test. This test is used to provide a quantifiable
resistance value for all of a product's insulation.
The test voltage is applied in the same fashion as a
standard Hipot test, but is specified to be Direct Current
(DC). The voltage and measured current value are used
to calculate the resistance of the insulation.
Hipot
Tester
A
hipot tester is an electronic device used to verify
the electrical insulation in a cable, printed circuit
board, electric motor, transformer or other wired assembly.
A Hipot tester is used to perform a high potential test.
Generally a hipot tester consists of:
A
source of high voltage,
A current meter,
A switching matrix used to connect the high voltage
source and the current meter to all of the contact points
in a cable.
In addition to these parts a hipot tester may also have
a microcontroller and a display to automate the testing
process and display the testing results. A hipot tester
can be very similar to a cable tester and often the
two are combined into a single device. A hipot tester
is used to verify that circuits that should be insulated
are well isolated. It does this by applying a high voltage
between the circuits and making sure no current flows.
In
a typical wired assembly a hipot test should connect
all circuits in common to ground. Then, one by one the
tester will disconnect a given circuit from ground and
connect that circuit to high voltage. The current that
flows is monitored to verify that it is low enough.
Hipot
Test Procedures
Products
being designed today usually must comply with product
safety regulations. Some of these regulations work to
reduce the chance of you receiving a harmful electrical
shock. Modern equipment is more likely to follow these
regulations. When it comes to hipot charge, energy,
and voltage you should select the "safest"
machine that will still test your cables.
To
minimize your risk of injury from electrical shock make
sure your hipot equipment follows these guidelines:
The
total charge you can receive in a shock should not exceed
45 uC.
The total hipot energy should not exceed 350 mJ.
The total current should not exceed 5 mA peak (3.5 mA
rms)
The fault current should not stay on longer than 10
mS.
If the tester doesn't meet these requirements then make
sure it has a safety interlock system that guarantees
you can not contact the cable while it is being hipot
tested.
These guidelines come from the test standard EN61010-1,
Safety requirements for electrical equipment for measurement,
control and laboratory use, April 1993, CENELEC. Over
the last decade many of the safety regulations have
been harmonized (standardized) and EN61010-1 is similar
to UL 61010A-1 (formerly UL3101-1).
While
you are testing cables there are several things you
can do to reduce the risk even more:
Verify
the correct operation of the safety circuits in the
equipment every time you calibrate it.
Follow all of the manufacturer's instructions and safety
guidelines.
Don't touch the cable during hipot testing.
Allow the hipot testing to complete before removing
the cable.
Wear insulating gloves.
If you have any health condition that can be aggravated
by being startled then don't use the equipment.
Don't allow children to use the equipment.
If you have any electronic implants then don't use the
equipment.
During
Test Where To Apply High Voltage?
To
understand a how hipot testing works you'll need to
understand where to connect the high voltage supply.
Hipot testers usually connect one side of the supply
to safety ground (Earth ground). The other side of the
supply is connected to the conductor being hipoted.
With the supply connected like this there are two places
a given conductor can be connected: high voltage or
ground.
When
you have more than two contacts to be hipot tested you
connect one contact to high voltage and connect all
other contacts to ground. Testing a contact in this
fashion makes sure it is isolated from all other contacts.
What
happens when you test something more complicated than
just contacts? A series of contacts that are connected
with wires, resistors, capacitors, diodes, and other
components is called a "network" of connections
(or "net"). To hipot test a net you connect
all of the contacts in the net to high voltage and connect
all other contacts in the device to ground. For example,
if you have a wire that connects two pins, the high
voltage will be simultaneously apply to both of those
pins and the entire wire will be raised in voltage.
All other wires and pins will be held at ground. If
you have a resistor that connects two pins, both pins
are raised in voltage, the voltage drop across the resistor
is always zero. The entire resistor is raised in voltage.
In short, all pins of a component see the same voltage
at all times. Applying the voltage in this fashion makes
sure the body of the component is isolated from the
rest of the device.
Where is the current measured?
During
the hipot test the current that flows out of the high
voltage supply is measured.
Xmultiple
HiPot test procedure includes testing the current at
2 mA amd 5 mA for connectors and parts requiring this
testing.
There are 2 sets of coils (Transmit & Receive) wich
are tested. We test both coils together.
What causes current to flow through an insulator?
Insulation
"does not conduct." But if you use enough
voltage even the best of insulations will allow some
current to flow. You may wonder why the current flows?
There are several reasons current will flow through
insulation during a hipot test. Resistance, capacitance,
arcs, electrochemical effects, and corona are all effects
that describe current flow. All of these effects add
together during a hipot test to shape the outcome of
the test.
Is
this answer helpful?